BLAST BLANKET
TESTS ON NETWORK
TRANSFORMER
APIC-2011
NETWORK TRANSFORMER
HV TERM WIPE
SLEEVE
HV TERM
COMP.
HV
SWITCH
COMP.
NETWORK
PROTECTOR
NTWK PROTECTOR
LOW VOLTAGE
TERMINAL
NETWORK
PROTECTOR
BLAST PRESSURE
BUILDINGS ARE DESIGNED FOR A WIND
PRESSURE OF : 34 LBS/M2 0.24PSI
@ 1 METRE a 25 KA ARC WOULD CREATE A
PRESSURE OF 0.29 PSI
COMBUSITON OF OIL-AIR MIXTURE IN A
41M3 VOLUME WOULD RELEASE 162MJ
HEAT ENERGY AND THE PRESSURE RISE
WOULD BE 14.5 ATM
1ATM = 101.325 KPa = 14.69 psi
HAZARD CATEGORY
NFPA 70E-2000
CAT 1 : 5 CAL/CM2
CAT 2 : 8 CAL/CM2
CAT 3 : 25 CAL/CM2
CAT 4 : 40 CAL/CM2
1 joule = 0.2338 cal
5 joules or 1.2 cal second degree curable burn
WHY BLAST BLANKETS
BLAST BLANKETS ARE SUPPOSED TO PROTECT A WORKER FROM THE HAZARD OF A FAILURE OF AN ENERGIZED NETWORK TRANSFORMER HV CHAMBER WHICH REQUIRES A CATEGORY 4 PROTECTION
BB- PROTECT BY DIVERTING OR BLOCKING THE BLASTS
PURPOSE OF THE TEST
TO FIND OUT THE BEST METHOD OF
INSTALLING BLAST BLANKETS.
TO PROTECT EPCOR CREWS WHILE
WORKING EITHER INSIDE AN ENERGIZED
NETWORK VAULT OR ON THE ROOF OF
AN ENERGIZED VAULT
TYPES OF BLAST BLANKETS
USED
TWO TYPES OF BLANKETS WERE
USED:
OBERON MAKE 25 KA BLAST
BLANKETS ( 8X5)’
SALISBURY MAKE 40 KA BLAST
BLANKETS (3X5)’
Installation details Top view
36”
Cal 1 @ 50” above
floor
56”
15”
45”
41”
9”
Cal 2 @ 40” above
floor
12.42”
White Cotton
White Cotton
62.42”
P1
P2
Specially built Vault used for
Testing
VAULT SIZE: 2.95 (W) X 3.3 (H) X 4.4 (D) m
VAULT SIZE: 2.95 (W) X 3.3 (H) X 4.2 (D) m (
vent ( 0.6m)
BB WRAP AROUND PETROLATUM
FILLED HV TERM COMP.
25 kA Oberon
blanket
wrapped
loosely on the
transformer
HV
compartment
Test 1 -videos
Play normal speed video: Test 10-2794
EPCOR\Blast Blanket Testing - June
2010\Normal Video\Test_10-2794.avi
Play HS video: Test HS:10-2794 EPCOR\Blast Blanket Testing - June 2010\HS
Video\HS10-2794.cine
BURNT PETROLATUM
MATERIAL SPLASHED
ONTO THE WALL
Burnt Petrolatum on the floor
TERMINATION CHAMBER
WALLS DEFOREMD, ITS
COVER BLOWN OFF AND
ALL THE BOLTS SHEARED
OFF.