Discussion on
“How to Report Your Stucco Observations
for All Panels”
Mock-Up Write-up Review:
Review of Home Inspector ReportWrite-ups:
What concerns or defects didyou report on Mock-Up Number_____?
What action did you suggest.
March 2009 © ESEC
Mock-Up 1 side A
What clues to the type of system are visible?
March 2009 © ESEC
Report Comments on Panel 1A
1. EIFS is crushed by surface mounted ledger and railing
support.
2. Improper flat top parapet walls.
3. Deck flashings are improper including missing end
dams.
4. Some water table flashings appear proper and others
appear to block drainage from MD-EIFS.
5. Some windows are sealed properly others are not
flashed and sealed both in the MD-EIFS and stone.
6. The bottom of the MD-EIFS is missing proper drainage.
7. OSB is visible between dissimilar materials.
8. The bottom of Manmade stone is improper in places.
March 2009 © ESEC
Report Comments on Panel 1A
(Cont.)We recommend that a full stucco inspection be
performed on this MD-EIFS house by an EDI
Certified Independent Third Party Inspector. All
issues relating to the MD-EIFS should be
properly corrected and that the repairs be
inspected by an EDI Certified Independent
Third Party Inspector. As with all homes,
ongoing periodic maintenance will be up to the
homeowner.
March 2009 © ESEC
Mock-Up 2 side A, Barrier or Face Sealed EIFS
What defects or concerns are visible?
March 2009 © ESEC
Report Comments on Panel 2A
1. Improper flat or low pitch top of parapet walls.
2. Deck flashings are improper including missing end
dams. Joints between deck framing and EIFS need to
be sealed.
3. All penetrations in EIFS need to be sealed.
4. Improper flat tops of accents are present.
5. The EIFS is not properly held above the roof covering.
6. Some windows are sealed properly others are not
flashed and sealed both in the EIFS and stone.
7. The bottom of EIFS does not properly lap foundation.
8. OSB is visible between dissimilar materials.
9. The bottom of Manmade stone is improper in places.
March 2009 © ESEC
Report Comments on Panel 2A
(Cont.)We recommend that a full stucco inspection be
performed on this Barrier or Face Seal EIFS
house by an EDI Certified Independent Third
Party Inspector. All issues relating to the
Barrier or Face Seal EIFS should be properly
corrected and that the repairs be inspected by
an EDI Certified Independent Third Party
Inspector. As with all homes, ongoing periodic
maintenance will be up to the homeowner.
March 2009 © ESEC
Mock-Up 2 side B; HCS over Insulation
What concerns or defects of the systems are visible?
March 2009 © ESEC
Report Comments on Panel 2B
1. This is a HCS system installed over EPS (or XPS)
insulation with no isolation joints at windows.
2. Improper flat topped sills are present.
3. The windows are not flashed and sealed to the HCS.
4. Window weep holes appear to be blocked.
5. The bottom of HCS does not properly lap foundation.
6. OSB is visible between dissimilar materials.
7. The bottom of Manmade stone is improper in places.
March 2009 © ESEC
Report Comments on Panel 2B(Cont.)
We recommend that a full stucco inspection be
performed on this house with HCS system
applied over EPS (or XPS); the inspection
should be performed by an EDI Certified
Independent Third Party Inspector. All issues
relating to the HCS should be properly
corrected and that the repairs be inspected by
an EDI Certified Independent Third Party
Inspector. As with all homes, ongoing periodic
maintenance will be up to the homeowner.
March 2009 © ESEC
Mock-Up 3 side A; HCS
What concerns or defects are visible in the system?
March 2009 © ESEC
Report Comments on Panel 3A
1. Some kickout flashings are improper or missing.
2. Deck flashings are improper including missing end
dams. Joints between deck framing and HCS need to
be sealed.
3. All penetrations in HCS need to be sealed.
4. Improper flat tops of accents are present.
5. Some HCS is not properly held above roof covering.
6. Some windows are sealed properly others are not
flashed and sealed both in HCS and manmade stone.
7. The bottom of HCS does not properly lap foundation.
8. OSB is visible between dissimilar materials.
9. The bottom of Manmade stone is improper in places.
March 2009 © ESEC
Report Comments on Panel 3A
(Cont.)We recommend that a full stucco inspection be
performed on this HCS house by an EDI
Certified Independent Third Party Inspector. All
issues relating to the HCS should be properly
corrected and that the repairs be inspected by
an EDI Certified Independent Third Party
Inspector. As with all homes, ongoing periodic
maintenance will be up to the homeowner.
March 2009 © ESEC
Mock-Up 4 side a
What concerns or defects are visible in this DA system?
March 2009 © ESEC
Report Comments on Panel 4A
This is a Direct Applied Exterior Finish
System (DEFS) or DA system:
1. DA system does not lap top of
foundation.
2. DA system is not sealed to penetrations.
3. DA system is not sealed to window jambs
and sills.
4. No control or expansion joints in the DA
system.
March 2009 © ESEC
Report Comments on Panel 4A(Cont.)
We recommend that a full stucco inspection be
performed on this DEFS or DA clad house by
an EDI Certified Independent Third Party
Inspector. All issues relating to the DEFS or
DA system should be properly corrected and
that the repairs be inspected by an EDI
Certified Independent Third Party Inspector. As
with all homes, ongoing periodic maintenance
will be up to the homeowner.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
What concerns or defects are present in these
3 or 4 systems.
March 2009 © ESEC
Report Comments on Panel 4B
1. System appears to be an improper EIFS at upper right
corner; a substrate is required.
2. The lower left section is a DA system with no substrate
or Moisture Resistive Barrier; does not meet current
standards.
3. The next section over is the next evolution of DA with a
Moisture Resistive Barrier behind the cement board.
4. The center section under the window is a Hard-Coat
Stucco system over a Moisture Resistive Barrier on
open framing; this is approved by most manufacturers.
5. The far right lower corner is an atypical stucco system
installed over non-approved wires rather than lath.
March 2009 © ESEC
Report Comments on Panel 4B
(Cont.)We recommend that a full stucco inspection be
performed on this ______clad house by an EDI
Certified Independent Third Party Inspector. All
issues relating to the ______ system should be
properly corrected and that the repairs be
inspected by an EDI Certified Independent
Third Party Inspector. As with all homes,
ongoing periodic maintenance will be up to the
homeowner.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
Improper Barrier EIFS on open studs. Note: if
Polyisocyanurate Insulation then this could be
an old PI system.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
Old DEFS or DA system on open framing with
no moisture resistive barrier and only cement
board joints taped. Fails current DA
installation specifications.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
DEFS or DA system on open framing with
moisture resistive barrier and only cement
board joints taped. Fails current DA
installation specifications.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
Hard Coat Stucco on open framing with Weather Resistive
Barrier, stucco netting, scratch coat and brown coat.
March 2009 © ESEC
Mock-Up 4 side b; Open Framing
Old Hard Coat Stucco on open framing with Weather
Resistive Barrier, stucco wires run between nails into
studs, scratch coat and brown coat.
March 2009 © ESEC
Mock-Up 5 side a; Moisture Resistive Barriers
Moisture Barriers
Tyvek Stucco Wrap & JumboTex D paper
March 2009 © ESEC
Report Comments on Panel 5A & 5B
1. Jamb flashing papers are atypical
2. The head flashing paper should be
shingled under the moisture resistive
barrier above.
3. The horizontal splices in the moisture
resistive barrier appear to be splice with
the appropriate minimum lap of 2 inches.
4. The vertical splices are not lapped the
required 6 inches.
March 2009 © ESEC
Report Comments on Panel 5A & 5B (Cont.)
We recommend that a full stucco inspection be
performed on this ______clad house by an EDI
Certified Independent Third Party Inspector. All
issues relating to the ______ system should be
properly corrected and that the repairs be
inspected by an EDI Certified Independent
Third Party Inspector. As with all homes,
ongoing periodic maintenance will be up to the
homeowner.
March 2009 © ESEC
Mock-Up 5 side a; Moisture Resistive Barriers
Flexible window flashing paper is properly
shingled over paper below sill. Jamb is
atypical; jamb flashing paper normally on top
of jamb nail fin.
March 2009 © ESEC
Mock-Up 5 side a; Moisture Resistive Barriers
Flexible flashing paper is improperly installed at
window head. It should be shingled under the
Moisture Resistive Barrier from above and
shingled over the window head nailing fin.
March 2009 © ESEC
Mock-Up 5 side a; Moisture Resistive Barriers
Horizontal shingling of building paper exceeds 2
inch minimum requirement.
March 2009 © ESEC
Mock-Up 5 side a; Moisture Resistive Barriers
Vertical splice lap of building paper is only about 2 inches
instead of the required minimum lap of 6 inches.
March 2009 © ESEC
Mock-Up 5 side B; Moisture Resistive Barriers
Liquid applied moisture resistive barrier; seams in
substrate taped and sealed then entire wall sealed.
March 2009 © ESEC
Mock-Up 5 side b; Moisture Resistive Barriers
DensGlass Gold with seams prepared taped and
sealed with Liquid Applied membrane.
March 2009 © ESEC