APPROVED QURAYYAH COMBINED CYCLE POWER PLANT – PROJECT C - CONVERSION OF OPEN CYCLE GAS TURBINES TO COMBINED CYCLE PLANT PTS # 07EG908 Volume 1 OF 3 Page 213 of 481 AlexV JAMIL M AL-MUTAIRI, MANAGER, EPED All metal in contact with seawater, including coarse screens, fine screens, cooling water pumps, valves and pipework and any sheet piling associated with the cooling water system and also buried metal structure and tank bases shall be equipped with cathodic protection. The cathodic protection system shall be complete in all respects and fully automatic. For seawater platinized titanium electrodes and zinc reference and sensing electrodes shall be used. For buried structures appropriate anode materials shall be used for the ground beds and reference electrodes as advised by the relevant standards. Contractor C shall, after commissioning the system, produce a report demonstrating that all buried pipework, equipment tank bases and metal in contact with seawater are suitably protected from corrosion. 6.8.3 Design and operating particulars Contractor C shall supply equipment according to the standards taking into account specific particulars detailed below: For design purposes the following minimum current densities shall be used for surfaces in contact with seawater. a. bare steel surfaces – 100 m A/m2 b. coated steel surfaces – 50 m A/m 2 The design minimum current densities shall be used for buried steel structures shall be: i. uncoated pipes and bare steel surfaces – 50 m A/m 2 ii. coated pipes – 2.5 m A/m 2 iii. external surfaces of tank bottoms – 20 m A/m 2 . The transformer/rectifier units shall have at least 50 per cent spare capacity over design. 6.8.4 Transformer rectifiers and control equipment The transformers associated with the rectifier units shall be of the double wound air insulated type with an earthed metal screen provided between the primary and secondary windings. The equipment shall incorporate means for protecting transformers and rectifiers against damage due to overload or short- circuit of the dc output. The rectifiers shall be three phase full-wave bridge connected type. The ripple content of the output wave shall not exceed 5 per cent rms over the entire output range. An approved surge diverter shall be connected across the dc terminals.

description

p

Transcript of T213

Page 1: T213

APPROVED QURAYYAH COMBINED CYCLE POWER PLANT –

PROJECT C - CONVERSION OF OPEN CYCLE GAS TURBINES TO COMBINED CYCLE PLANT

PTS # 07EG908 Volume 1 OF 3

Page 213 of 481

AlexV

JAMIL M AL-MUTAIRI, MANAGER, EPED

All metal in contact with seawater, including coarse screens, fine screens, cooling water pumps, valves and pipework and any sheet piling associated with the cooling water system and also buried metal structure and tank bases shall be equipped with cathodic protection. The cathodic protection system shall be complete in all respects and fully automatic. For seawater platinized titanium electrodes and zinc reference and sensing electrodes shall be used. For buried structures appropriate anode materials shall be used for the ground beds and reference electrodes as advised by the relevant standards.

Contractor C shall, after commissioning the system, produce a report demonstrating that all buried pipework, equipment tank bases and metal in contact with seawater are suitably protected from corrosion.

6.8.3 Design and operating particulars

Contractor C shall supply equipment according to the standards taking into account specific particulars detailed below:

For design purposes the following minimum current densities shall be used for surfaces in contact with seawater.

a. bare steel surfaces – 100 m A/m2

b. coated steel surfaces – 50 m A/m2

The design minimum current densities shall be used for buried steel structures shall be:

i. uncoated pipes and bare steel surfaces – 50 m A/m2

ii. coated pipes – 2.5 m A/m2

iii. external surfaces of tank bottoms – 20 m A/m2.

The transformer/rectifier units shall have at least 50 per cent spare capacity over design.

6.8.4 Transformer rectifiers and control equipment

The transformers associated with the rectifier units shall be of the double wound air insulated type with an earthed metal screen provided between the primary and secondary windings. The equipment shall incorporate means for protecting transformers and rectifiers against damage due to overload or short-circuit of the dc output. The rectifiers shall be three phase full-wave bridge connected type. The ripple content of the output wave shall not exceed 5 per cent rms over the entire output range. An approved surge diverter shall be connected across the dc terminals.

S.kenderjian
Sticky Note
MOM BOP MECH #021 Tenderer Comment Contractor will not produce such a report. SEC Response Not accepted. Bidder shall comply with the PTS requirements. Tenderer Response Report demonstrating suitable protection for equipment can be produced during commissioning, except for buried equipment (underground or offshore) not having monitoring facility to relay the reading of the anodes. SEC 2nd Response The Bidder shall provide a suitable cathodic protection system, including monitoring system, for all underground and offshore equipment, shall also submit report during commissioning. Tenderer Response Noted Meeting Resolution Noted.