Power Transformer Maintenance
Maintenance Practices & Procedures for Substation
Class Distribution Power Transformers
Power Transformer Maintenance
Why should special maintenance practices be
applied to power transformers?
• Power transformers utilize active cooling systems
• Equipped with additional monitoring and
protection equipment
• Represent a large capital investment
• Often serve critical customers who suffer very
large financial losses in the case of transformer
failure
• Spare power transformers are typically not
available and replacements can take several
months
Power Transformer Maintenance
Why should special maintenance practices be
applied to power transformers?
• IEEE/ANSI consider average transformer life to be
20-25 years based on the assumption that
adequate maintenance is performed over their
service life.
• IEEE life based on a continual ambient
temperature of 40º C and temperature rise of 65º C
• Due to lower ambient temperatures and lower
temperature rises in typical distribution
conditions, transformer life can be extended to 40
years or more with proper monitoring and
maintenance.
Power Transformer Maintenance
Why should special maintenance practices be
applied to power transformers?
Power Transformer Maintenance
• Operation at only 10% above the transformer
temperature rating will cut transformer life by 50%
• Transformer heating by:
• Internal losses due to loading
• High ambient temperature
• Solar radiation
• FortisAlberta makes use of ONAN/ONAF/ONAF
cooling systems on power transformers.
• ONAN – Oil Natural/Air Natural
• ONAF – Oil Natural/Air Forced
Power Transformer Maintenance
Inspection of ONAF Equipped Power Transformers
• Performed after 1 month of service and yearly
• Visible leaks and/or corrosion
• Shutoff valve position on radiators
• Fans
• Radiators
• Bushings
• Gaskets
• Top oil thermometer
• Winding temperature thermometer
• Thermometer testing every 3-5 years
Power Transformer Maintenance
Inspection of ONAF Equipped Power Transformers
• Inspection after 1 month and every 3-5 years
• Oil Level Indicator
Power Transformer Maintenance
Inspection of ONAF Equipped Power Transformers
• Inspected after 1 month of service and yearly
• Pressure relief device
Power Transformer Maintenance
Inspection of ONAF Equipped Power Transformers
• Inspected after 1 month of service and yearly
• Sudden Pressure Relay
Power Transformer Maintenance
Sealed Breathing System
• Allows ‘breathing’ to the atmosphere when pre-set
pressure gradients are surpassed
• Can lead to oil contamination
Power Transformer Maintenance
Electrical Testing of Power Transformers
• Performed before energizing and every 3-5 years
• Factory testing records should be kept as
baseline records
• Testing done before energizing to ensure no
damage occurred during shipping and as
confirmation of factory testing
• Test throughout the life of the transformer
when customer shutdowns or outages allow
• Test when a known fault has occurred
Power Transformer Maintenance
Insulating Power Factor Test
• Provides overall test of the insulating properties
of a transformer
• Measures the power losses due to leakage current
through the insulation
Turns Ratio Test
• Can detect shorted turns in the windings or a
defective tap changer
• Early indication of transformer failure
Power Transformer Maintenance
Winding Resistance Test
• Direct current evaluation test of the insulation
• Reliable indication of the presence of moisture,
contamination, or breakdown in the insulation
Core Insulation Resistance Test
• Measured by standard ‘megger’ test
• Core ground must be disconnected prior to test
• Detects deteriorating insulation between the core
and ground
Power Transformer Maintenance
Transformer Oils
• Transformer oils perform at least three functions
for the transformer:
• Provides Insulation
• Provides Cooling
• Helps extinguish arcs
• Oils also dissolve elements that can be measured
for analysis from:
• Oil degradation
• Moisture and gas from cellulose insulation
degradation
• Gases and moisture from whatever
atmosphere the oil is exposed to
Power Transformer Maintenance
Dissolved Gases in Transformer Oil
• Close observation of dissolved gases in the oil,
and other oil properties, PROVIDE THE MOST
VALUABLE INFORMATION REGARDING
TRANSFORMER HEALTH
• Oil samples should be taken and sent to a
qualified lab for analysis prior to energizing, one
month into service and yearly thereafter
• Great care must be taken to ensure that the
sample does not become contaminated and is not
exposed to the atmosphere
Power Transformer Maintenance
Dissolved Gases Analysis (DGA) is the most
valuable diagnostic tool available as part of a
transformer maintenance schedule.
•It is paramount that accurate records of DGA for
each individual transformer are kept as trends in gas
concentration changes are far more valuable than
individual gas concentrations.
• A sudden increase in key gases and the rate
of gas production is more important in
evaluating a transformer than the amount of
gas present in a DGA
• The exception to this is the presence of
Acetylene (C2H2)
Power Transformer Maintenance
IEEE C57-104 outlines a method of interpreting DGA
known as the ‘Key Gas Method’
•This method sets conditions that coincide with
given concentrations of gases and outlines
recommended actions based on these
concentrations and their generation rates
•Key Gases are:
• Hydrogen (H2)
• Methane (CH4)
• Ethane (C2H6)
• Ethylene (C2H4)
• Acetylene (C2H2)
• Carbon Monoxide (CO)
• Carbon Dioxide (CO2)
• Oxygen (O2)
Power Transformer Maintenance
Large concentrations of Nitrogen (N2), near
saturation, can also be discovered through DGA, but
present no concern as this is due to the nitrogen gas
blanket that is injected in the tank above the oil by
the manufacturer.
Large concentrations of atmospheric gasses (N2,
CO2, O2) can be very valuable in DGA in revealing a
possible leak.
The presence of Acetylene (C2H2), and to a lesser
extent Ethylene (C2H4), in concentrations higher than
trace levels should be further investigated as these
gases typically are only produced under arching
conditions.
Power Transformer Maintenance
Moisture Problems
• Each time the moisture is doubled in paper
insulation, the life of the transformer is cut in half.
• The life of the transformer IS the life of the paper!
• Keeping the water and oxygen levels in a
transformer to a minimum will greatly extend the
life of a transformer.
• The sealed breathing tank system creates the
possibility of moisture and oxygen problems as
the external atmosphere will be allowed to enter
the tank under conditions where the tank is in
vacuum.
Power Transformer Maintenance
Moisture Problems
• Moisture, especially in the presence of oxygen, is
extremely hazardous to cellulose transformer
insulation
• Each DGA or Insulating Power Factor Test should
be analyzed to determine the moisture by dry
weight (M/DW) that is present in the paper
insulation
• New transformers typically have a M/DW
under 0.5%
• Plans should be made to dry out the
transformer insulation once a M/DW of 2%
has been reached.
• An M/DW value of 4% presents a great
danger of flashover
Power Transformer Maintenance
Moisture Problems
• Moisture causes insulation to decay, which forms
more moisture, acids and sludge
• The additional moisture and acids further
increase the rate of insulation decay
• Sludge coats the coils and radiators,
leading to a slowly rising operating
temperature for a given load and ambient
temperature
• Both of these conditions lead to
exponentially increasing insulation decay if
steps are not taken to dry out the
transformer.
Power Transformer Maintenance
Where does the water come from?
•Some moisture is in the insulation when it is
delivered from the factory
•Atmospheric moisture can enter the transformer
when it is opened for inspection or through the
breather system when the tank is in vacuum
•Rain or atmospheric moisture can enter the tank
through leaky gaskets, especially during times of
rapid transformer cooling when a vacuum is created
inside the tank
Power Transformer Maintenance
Additional Oil Tests the be performed with DGA
• Dielectric Strength Test
• Measures the voltage
at which the oil
electrically breaks down.
• Gives a good indication
of contaminants in the oil
• As per ASTM Test Method D-877 or D-1816
• Interfacial Tension Test (IFT)
• Determines interfacial tension between
distilled water and oil
• Measures concentration of particles in the
oil
Power Transformer Maintenance
Additional Oil Tests the be performed with DGA
•Acid Number Test
• Measures the amount of potassium
hydroxide required to neutralize acid in the
oil.
•Test for Oxygen Inhibitor (every 3-5 years)
• Determines level of inhibitor present
• The inhibitor acts as a sacrificial substance
that the oxygen will react with rather than
with metal or paper within the transformer.
•Power Factor Test
• Indicates dielectric loss (leakage current) if
‘Doble Test’ is not available
• Power factor should be maintained at less
than 0.5% at 25° C